Concrete in Compression (ACI 318)

In general, the behavior of a reinforced concrete member under load depends on the stress-strain relationship of concrete and reinforcement, as well as the type and duration of loading. Because engineers use concrete principally in compression, its compressive stress-strain curve is of primary interest.

Code edition: At present, ACI CODE-318-25 is the current ACI structural concrete code. However, the equations below are educational summaries; design work must use the edition adopted by the governing building code and the project documents.

What Does f’c Mean?

Engineers write the specified compressive strength of concrete as f’c. For example, they normally base it on the strength of standard cylinders tested at the specified age, commonly 28 days. Also, ASTM C39/C39M-26 gives the current test method for compressive strength of cylindrical concrete specimens.

Therefore, report strength in MPa or psi. One MPa is equal to one N/mm2.

Then, calculate the cylinder strength by dividing the maximum load by the measured cross-sectional area:

fc = P / A = 4P / (πD2)

However, do not confuse this measured test result with every value used in structural design. The specified strength, average test result, required average strength, and in-place strength have different meanings.

Concrete Stress-Strain Curve in Compression

Illustrative compressive stress-strain curves for normal-strength and higher-strength concrete
Illustrative curves. Higher-strength concrete usually has a steeper ascending branch and a more brittle descending branch.

First, the curve is not a straight line. Its initial slope is relatively steep; then, the stiffness decreases as microcracking develops. Finally, normal-strength concrete commonly reaches its maximum stress at a strain near 0.002, but the exact value depends on the mixture, strength, aggregate, loading rate, and test conditions.

In comparison, higher-strength concrete is generally more brittle and has a steeper descending branch than lower-strength concrete. However, the peak strain is not the same thing as the design ultimate compressive strain.

Do not mix the values: for example, engineers often associate a strain near 0.002 with peak cylinder stress. In contrast, the familiar ACI rectangular stress-block model uses an extreme concrete compression strain of 0.003 at nominal strength. Therefore, treat that as a design assumption, not a statement that every test cylinder fails at exactly 0.003.

Modulus of Elasticity of Concrete

Concrete does not have one constant slope over its complete stress-strain curve. Therefore, ACI uses an empirical expression for the modulus of elasticity, Ec.

US Customary Units

For concrete with unit weight wc from 90 to 160 lb/ft3:

Ec = 33 wc1.5 √f’c

Here, Ec and f’c are in psi. For normal-weight concrete, the commonly used simplified form is:

Ec = 57,000 √f’c psi

SI Units

Similarly, for concrete density wc from 1440 to 2560 kg/m3:

Ec = 0.043 wc1.5 √f’c MPa

Therefore, for normal-weight concrete, the simplified SI expression is:

Ec = 4700 √f’c MPa

In practice, these expressions estimate static modulus for design. They appear in ACI CODE-318-25, Section 19.2.2.1. However, use ASTM C469/C469M-22 when you require a measured chord modulus and Poisson’s ratio.

Concrete Modulus of Elasticity Calculator




Density-based ACI range: 1440 to 2560 kg/m3.

Estimated Ec: 27,691 MPa
Equivalent: 27.69 GPa

Worked Example

For example, consider normal-weight concrete with f’c = 30 MPa:

Ec = 4700 √30 = 25,743 MPa = 25.74 GPa

Meanwhile, the density-based expression with 2400 kg/m3 gives approximately 27.69 GPa. Therefore, remember that the two equations are empirical estimates and need not give identical results.

Factors That Change the Compression Curve

Factor Typical effect
Concrete strength and mixture Changes the peak stress, initial slope, and post-peak brittleness
Aggregate type Strongly affects stiffness and the shape of the curve
Moisture and curing Affects strength development and measured stiffness
Loading rate Faster loading commonly gives a higher measured peak strength
Specimen geometry and end condition Changes restraint, stress distribution, and the measured result
Confinement Can increase usable compressive strain and ductility

Strength Development and Creep

Concrete strength changes with time. For example, the specified strength is often based on 28 days, but the actual rate of gain depends on cementitious materials, temperature, curing, and mixture proportions. Therefore, fixed statements such as “every concrete reaches 70% at 7 days” are only rough rules and should not be used for acceptance.

In addition, concrete continues to deform with time under a sustained compressive stress. Engineers call this behavior creep. Creep depends on stress level, age at loading, member size, humidity, mixture proportions, and duration of loading. Therefore, consider it together with shrinkage in serviceability calculations.

References and Related Articles