Engineers commonly perform this test on concrete in construction because it gives a general idea about the characteristics of concrete. Based on this test and the applicable acceptance criteria, one can accept the concrete or decide that further evaluation is required.
Also, compressive strength as a concrete property depends on several factors related to the quality of the materials, mix design, sampling, curing, specimen preparation, and quality control during concrete production.
Compressive Strength Test Formula
fc = P / A

When the load is measured in newtons and the area is measured in square millimetres, the result is N/mm2, which is equal to MPa.
Cube Test or Cylinder Test?
Depending on the applied code, the test specimen may be a cylinder [150 mm diameter x 300 mm high is common] or a cube [150 mm x 150 mm x 150 mm is common]. For example, ASTM C39/C39M covers cylindrical concrete specimens. Cube testing follows the standard specified for the project.
Do not directly compare cube and cylinder results as if they are identical. Specimen shape, dimensions, end preparation, curing, and loading procedure affect the measured strength.
Relation Between Cube and Cylinder Strength
For normal-strength concrete, the cylinder result is commonly lower than the cube result. The shorter cube receives more restraint from the machine platens, while a cylinder has a larger unrestrained zone. However, there is no one conversion factor that is accurate for every concrete. The ratio changes with the concrete strength, specimen size, aggregate, end preparation, curing, and test procedure.
As a quick approximation, engineers sometimes take the cylinder strength as about 80% of the cube strength. Use this only as a rough comparison. For design or acceptance, use the strength class and specimen shape stated in the applicable code and project specification.
| Concrete class | Characteristic cylinder strength | Characteristic cube strength |
|---|---|---|
| C20/25 | 20 MPa | 25 MPa |
| C25/30 | 25 MPa | 30 MPa |
| C30/37 | 30 MPa | 37 MPa |
| C35/45 | 35 MPa | 45 MPa |
| C40/50 | 40 MPa | 50 MPa |
For example, C25/30 means a characteristic cylinder strength of 25 MPa and a characteristic cube strength of 30 MPa. These are paired strength-class values. They are not a rule for converting one individual test result into the other.
Compressive Strength Test Idea
- First, technicians sample the concrete, place it in the mould, and consolidate it according to the applicable standard.
- Next, technicians remove the moulds after the initial curing period and store the specimens under the specified curing conditions.
- Then, at the specified test age, the technician checks the dimensions and condition of each specimen.
- After that, the technician centres the specimen in the compression testing machine and applies the load continuously at the rate required by the applicable test standard.
- Finally, record the maximum load. Then, divide the failure load by the loaded cross-sectional area.
Apparatus
- Compression testing machine with suitable capacity and current verification
- Cube or cylinder moulds that meet the specified dimensions and tolerances
- Sampling and mixing equipment, when specimens are prepared in a laboratory
- Compaction equipment required by the applicable standard
- Trowel, scoop, measuring tools, identification labels, and curing facilities
Sample Preparation
Technicians take samples from the concrete used on site or prepare them from a laboratory batch. The sampling method is important because the specimen must represent the concrete being evaluated.
Common specimen sizes: cylinders 150 mm x 300 mm or cubes 150 mm x 150 mm x 150 mm. However, the standard may permit other sizes according to the nominal maximum aggregate size.
The applicable standard and project specification determine the number of specimens, the ages of testing, and how individual results form one strength test. Therefore, do not assume that three specimens are required in every code.
Mixing Concrete
You may mix concrete in a laboratory batch mixer. When the standard permits hand mixing, first mix the cement and fine aggregate until the mixture is thoroughly blended. Then, add the coarse aggregate and mix until it is uniformly distributed. Finally, add water and mix until the concrete appears homogeneous and has the required consistency.
Placing Concrete in Moulds
- Clean the moulds and apply the permitted release agent without leaving excess oil.
- Fill and consolidate the concrete in the number of layers and by the method required by the standard. Do not use a fixed number of strokes from a different test method.
- Finish the top surface and identify the specimen without damaging it.
Curing
Store the moulded specimens under the required initial-curing conditions. After demoulding, continue standard curing until the test age. Record any departure from the specified temperature, moisture condition, or timing because poor curing can reduce the measured strength.
Compressive Strength Test Procedure
- First, remove the specimen from curing and wipe off surface water.
- Next, confirm the specimen identification, age, dimensions, and end condition.
- Then, clean the bearing faces of the specimen and testing machine.
- After that, place and centre the specimen correctly. For a cube, apply load to the faces specified by the applicable standard. For a cylinder, use the required capped, ground, or unbonded end treatment.
- Next, apply the load continuously and without shock at the test standard’s specified rate.
- Finally, record the maximum load and note the failure pattern or any unusual condition.
- Then, calculate and report the compressive strength using the measured loaded area.
Cube Compressive Strength Example
Assume a 150 mm concrete cube failed at a maximum load of 720 kN.
| Item | Calculation | Result |
|---|---|---|
| Loaded area | 150 x 150 | 22,500 mm2 |
| Failure load | 720 kN x 1,000 | 720,000 N |
| Compressive strength | 720,000 / 22,500 | 32.0 N/mm2 = 32.0 MPa |
Cylinder Compressive Strength Example
Assume a concrete cylinder with an average measured diameter of 150 mm failed at a maximum load of 600 kN.
| Item | Calculation | Result |
|---|---|---|
| Loaded area | π x 1502 / 4 | 17,671 mm2 |
| Failure load | 600 kN x 1,000 | 600,000 N |
| Compressive strength | 600,000 / 17,671 | 34.0 N/mm2 = 34.0 MPa |
The cylinder area is calculated from the measured average diameter, not from the nominal diameter when the test standard requires measured dimensions.
What to Record in the Test Report
- Project, concrete mixture, sample, and specimn identification
- Sampling, casting, and testing dates and the specimen age
- Specimen type, nominal dimensions, and measured loaded area
- Curing and moisture condition
- End-preparation method for cylinders
- Maximum load and calculated compressive strength
- Failure pattern, defects, damage, or other unusual observations
- Test method and any deviation from it
Sample Compressive Strength Test Report
The following is a simple example of how the results can be arranged. Keep cube and cylinder results in separate groups, and do not average the two specimen shapes together.
| Project and Sample Information | |||
|---|---|---|---|
| Project | Office Building | Concrete location | First-floor columns |
| Mix identification | M-30-01 | Specified age | 28 days |
| Sampling date | 4 May 2026 | Testing date | 1 June 2026 |
| Specimen ID | Shape and size | Area | Failure load | Strength | Observation |
|---|---|---|---|---|---|
| CY-01 | Cylinder, 150 x 300 mm | 17,671 mm2 | 600 kN | 34.0 MPa | No visible defect before testing |
| CY-02 | Cylinder, 150 x 300 mm | 17,671 mm2 | 618 kN | 35.0 MPa | Fracture type recorded separately |
| CU-01 | Cube, 150 x 150 x 150 mm | 22,500 mm2 | 720 kN | 32.0 MPa | No visible defect before testing |
| CU-02 | Cube, 150 x 150 x 150 mm | 22,500 mm2 | 742.5 kN | 33.0 MPa | Failure pattern recorded separately |
Report note: the numbers above show the calculation and report format only. A real laboratory report must include the test method, curing condition, machine identification, end preparation, measured dimensions, failure pattern, defects, deviations, and the acceptance criteria required by the project.
Common Errors That Can Reduce the Result
- Poor or non-representative sampling
- Insufficient or excessive consolidation
- Loss of moisture or temperature outside the required curing range
- Damaged specimens or uneven bearing surfaces
- Incorrect centring or loading rate
- Using the wrong specimen area or incorrect unit conversion
How to Interpret the Result
A single specimen result is not automatically the acceptance decision for the concrete. The specified code defines how specimens form one strength test and how to evaluate groups of tests. If a result is low, check the sampling, curing, specimen condition, testing records, and acceptance provisions before deciding what action is required.
Also, 7-day results are useful for monitoring early strength development, but they are not automatically a fixed percentage of the 28-day strength. Cement type, supplementary cementitious materials, water-to-cement ratio, temperature, and curing can change the strength-development rate.
References
- ASTM C39/C39M, Standard Test Method for Compressive Strength of Cylindrical Concrete Specimens
- American Concrete Institute, Strength Testing Frequently Asked Questions
- Federal Highway Administration, Hardened Concrete Laboratory Manual
- The Concrete Centre, Eurocode 2 Frequently Asked Questions
Read Also:
Reasons for Testing Concrete Compressive Strength at 28 Days