Following the evaluation of the cracked structure, a suitable repair procedure can be selected. Successful
repair procedures take into account the cause(s) of the cracking. For example, if the cracking was primarily due to drying shrinkage, then it is likely that after a period of time the cracks will stabilize. On the other hand, if the cracks are due to a continuing foundation settlement, repair will be of no use until the settlement problem is corrected. 
In this series of articles under the title of “Methods of Crack Repair in Concrete“, the different techniques applied to repair cracks are discussed, starting with epoxy injection in this article.

⇒ Epoxy injection

Cracks as narrow as 0.05 mm can be bonded by the injection of epoxy. The technique generally consists of establishing entry and venting ports at close intervals along the cracks, sealing the crack on exposed surfaces, and injecting the epoxy under pressure. Epoxy injection has been successfully used in the repair of cracks in buildings, bridges, dams, and other types of concrete structures. However, unless the cause of the cracking has been corrected, it will probably recur near the original crack. If the cause of the cracks cannot be removed, then two options are available. One is to rout and seal the crack, thus treating it as a joint, or, establish a joint that will accommodate the movement and then inject the crack with epoxy or other suitable material. Epoxy materials used for structural repairs should conform to ASTM C 881 (Type IV).

With the exception of certain moisture tolerant epoxies, this technique is not applicable if the cracks are actively leaking and cannot be dried out. Wet cracks can be injected using moisture tolerant materials, but contaminants in the cracks (including silt and water) can reduce the effectiveness of the epoxy to structurally repair the cracks.

The use of a low-modulus, flexible adhesive in a crack will not allow significant movement of the concrete structure. The effective modulus of elasticity of a flexible adhesive in a crack is substantially the same as that of a rigid adhesive because of the thin layer of material and high lateral restraint imposed by the surrounding concrete.

Epoxy injection requires a high degree of skill for satisfactory execution, and application of the technique
may be limited by the ambient temperature. The general procedures involved in epoxy injection are as follows (ACI 503R):

1- Clean the cracks: The first step is to clean the cracks that have been contaminated., to the extent
this is possible and practical. Contaminants such as oil, grease, dirt, or fine particles of concrete prevent epoxy penetration and bonding, and reduce the effectiveness of repairs. Preferably, contamination should be removed by vacuuming or flushing with water or other specially effective cleaning solutions. The solution is then flushed out using compressed air and a neutralizing agent or adequate time is provided for air drying.

2- Seal the surfaces: Surface cracks should be sealed to keep the epoxy from leaking out before it has gelled. Where the crack face cannot be reached, but where there is back-fill, or where a slab-on-grade is being repaired, the back-fill material or sub-base material is sometimes an adequate seal; however, such a condition can rarely be determined in advance, and uncontrolled injection can cause damage such as plugging a drainage system. Extreme caution must therefore be exercised when injecting cracks that are not visible on all surfaces. A surface can be sealed by applying an epoxy, polyester, or other appropriate sealing material to the surface of the crack and allowing it to harden. If a permanent glossy appearance along the crack is objectionable and if high injection pressure is not required, a strippable plastic surface sealer may be applied along the face of the crack. When the job is completed, the surface sealer can be stripped away to expose the gloss-free surface. Cementitious seals can also be used where appearance of the completed work is important. If extremely high injection pressures are needed, the crack can be cut out to a depth of 13 mm and width of about 20 mm in a V-shape, filled with an epoxy, and struck off flush with the surface.

3- Install the entry and venting ports. Three methods are in general use:

a. Fittings inserted into drilled holes. This method was the first to be used, and is often used in conjunction with V-grooving of the cracks. The method entails drilling a hole into the crack, approximately 20 mm in diameter and 13 to 25 mm below the apex of the V-grooved section, into which a fitting such as a pipe nipple or tire valve stem is usually bonded with an epoxy adhesive. A vacuum chuck and bit, or a watercooled corebit, is useful in preventing the cracks from being plugged with drilling dust.

b. Bonded flush fitting. When the cracks are not Vgrooved, a method frequently used to provide an entry port is to bond a fitting flush with the concrete face over the crack. The flush fitting has an opening at the top for the adhesive to enter and a flange at the bottom that is bonded to the concrete.

c. Interruption in seal. Another system of providing entry is to omit the seal from a portion of the crack. This method can be used when special gasket devices are available that cover the unsealed portion of the crack and allow injection of the adhesive directly into the crack without leaking.

4- Mix the epoxy. This is done either by batch or continuous methods. In batch mixing, the adhesive components are premixed according to the manufacturer’s instructions, usually with the use of a mechanical stirrer, like a paint mixing paddle. Care must be taken to mix only the amount of adhesive that can be used prior to commencement of gelling of the material. When the adhesive material begins to gel, its flow characteristics begin to change, and pressure injection becomes more and more difficult. In the continuous mixing system, the two liquid adhesive components pass through metering and driving pumps prior to passing through an automatic mixing head. The continuous mixing system allows the use of fast setting adhesives that have a short working life.

5- Inject the epoxy. Hydraulic pumps, paint pressure pots, or air-actuated caulking guns may be used. The pressure used for injection must be selected carefully. Increased pressure often does little to accelerate the rate of injection. In fact, the use of excessive pressure can propagate the existing cracks, causing additional damage. If the crack is vertical or inclined, the injection process should begin by pumping epoxy into the entry port at the lowest elevation until the epoxy level reaches the entry port above. The lower injection port is then capped, and the process is repeated until the crack has been completely filled and all ports have been capped. For horizontal cracks, the injection should proceed from one end of the crack to the other in the same manner. The crack is full if the pressure can be maintained. If the pressure can not be maintained, the epoxy is still flowing into unfilled portions or leaking out of the crack.

6- Remove the surface seal. After the injected epoxy has cured, the surface seal should be removed by grinding or other means as appropriate.

Example for Epoxy Injection Techniques (AdhesivesTechnology)

Alternative procedure. For massive structures, an alternate procedure consists of drilling a series of holes [usually 20 to 100-mm diameter] that intercepts the crack at a number of locations. Typically, holes are spaced at 1.5-m intervals.

Another method recently being used is a vacuum or vacuum assist method. There are two techniques: one is to entirely enclose the cracked member with a bag and introduce the liquid adhesive at the bottom and to apply a vacuum at the top. The other technique is to inject the cracks from one side and pull a vacuum from the other. Typically, epoxies are used; however, acrylics and polyesters have proven successful.

Methods of Crack Repair (2)

Methods of Crack Repair (3)

Methods of Crack Repair (4)

Source:  ACI 224.1R-93: Causes, Evaluation and Repair of Cracks in Concrete Structures

 