ASTM C128: Specific Gravity and Absorption Test for Fine Aggregate

ASTM C128

In concrete mix design, sand might not get the same attention as cement or gravel. But its absorption and specific gravity affect the batch water, aggregate volume, yield, and finally the concrete consistency.

ASTM C128 is the test used to determine the relative density (specific gravity) and absorption of fine aggregate. The current edition is ASTM C128-25. The four reported values are bulk specific gravity in the oven-dry condition, bulk specific gravity in the saturated surface-dry condition, apparent specific gravity, and absorption.

Important: Specific gravity is dimensionless. It is not the same as bulk density or unit weight, because bulk density includes the voids between aggregate particles.

What ASTM C128 Measures

  • Bulk specific gravity (oven-dry): uses the oven-dry mass and includes the permeable pores in the particle volume.
  • Bulk specific gravity (SSD): uses the saturated surface-dry mass.
  • Apparent specific gravity: excludes the volume of pores that water can enter.
  • Absorption: the increase in aggregate mass due to water inside the permeable pores, expressed as a percentage of the oven-dry mass.

These values are used in absolute-volume concrete mix calculations. For example, the aggregate volume cannot be calculated correctly unless the selected mass and the corresponding OD or SSD specific gravity are used on the same basis.

Apparatus for ASTM C128

  • Balance with the accuracy required by the current test method.
  • Pycnometer suitable for introducing the fine aggregate and removing air.
  • Metal cone mold, 40 mm diameter at the top, 90 mm diameter at the bottom, and 75 mm high.
  • Metal tamper with a flat circular face 25 mm in diameter.
  • Oven capable of maintaining 110 ± 5°C.
  • 4.75 mm (No. 4) sieve, tray, scoop, and a gentle source of moving air.
ASTM C128 fine aggregate cone test showing wet, saturated surface-dry, and too-dry conditions
The fine aggregate reaches SSD when the molded pile slumps slightly after the cone is lifted.

Preparing the Fine Aggregate Sample

  1. Obtain a representative fine aggregate sample and reduce it to the test size without losing any fraction.
  2. Dry the sample to constant mass at 110 ± 5°C, cool it, and cover it with water for the prescribed conditioning period.
  3. Decant the excess water carefully. Then spread the sample on a flat, nonabsorbent surface.
  4. Dry the sample gradually while stirring it frequently. A gentle current of warm air may be used, but do not heat one part of the sample more than another.

The standard laboratory reference is based on the prescribed 24-hour soaking condition. Aggregates conditioned by another approved method can give different absorption and SSD specific gravity values, so the conditioning method should be reported when it is not the standard condition.

How to Find the SSD Condition

  1. Place the cone on a smooth, nonabsorbent surface with the large opening down.
  2. Fill the cone loosely with the fine aggregate.
  3. Tamp the surface lightly 25 times. Allow the tamper to fall freely from the required small height; do not compact the sand heavily.
  4. Clear loose material from around the base and lift the cone vertically.

If the pile keeps the shape of the mold, surface moisture is still present. Continue drying and repeat the cone test. The first slight slump of the molded fine aggregate shows that the SSD condition has been reached.

If the sample slumps excessively on the first attempt, it may have dried past SSD. Add a small measured amount of water, mix it, cover it, and repeat the SSD determination according to the current standard.

ASTM C128 Test Procedure

  1. Immediately weigh the required SSD test portion. Record this mass as S.
  2. Place the SSD fine aggregate in the pycnometer and add water.
  3. Remove entrapped air by the procedure permitted for the pycnometer. Trapped bubbles make the calculated specific gravity wrong.
  4. Bring the pycnometer and contents to the required test temperature, fill to the calibration mark, dry the outside, and weigh. Record this mass as C.
  5. Determine the mass of the pycnometer filled with water to the same calibration mark at the same temperature. Record it as B.
  6. Remove the fine aggregate, dry it to constant mass at 110 ± 5°C, cool it, and weigh. Record the oven-dry mass as A.
Do not mix the symbols: A is oven-dry aggregate, S is SSD aggregate, B is pycnometer plus water, and C is pycnometer plus SSD aggregate plus water.

ASTM C128 Formulas

Result Formula
Bulk specific gravity (OD) A / (B + S – C)
Bulk specific gravity (SSD) S / (B + S – C)
Apparent specific gravity A / (B + A – C)
Absorption, % [(S – A) / A] × 100

Where:

  • A = mass of oven-dry fine aggregate in air, g
  • S = mass of SSD fine aggregate in air, g
  • B = mass of pycnometer filled with water, g
  • C = mass of pycnometer with SSD sample and water, g

ASTM C128 Calculator




Bulk SG (OD): 2.523

Bulk SG (SSD): 2.564

Apparent SG: 2.631

Absorption: 1.63%

Worked Example

Suppose the following laboratory masses were recorded:

  • A = 492 g
  • S = 500 g
  • B = 650 g
  • C = 955 g

First, calculate the bulk denominator:

B + S – C = 650 + 500 – 955 = 195 g

Result Substitution Answer
Bulk SG (OD) 492 / 195 2.523
Bulk SG (SSD) 500 / 195 2.564
Apparent SG 492 / (650 + 492 – 955) 2.631
Absorption [(500 – 492) / 492] × 100 1.63%

Common Errors in the Test

  • Wrong SSD judgment: this directly changes S and affects bulk SSD specific gravity and absorption.
  • Trapped air: bubbles increase the measured volume displacement error.
  • Different water temperatures: B and C should be determined under the required temperature conditions.
  • Loss of fine particles: losing material while decanting, transferring, or drying changes the result.
  • Wet pycnometer exterior: water on the outside is added to the measured mass.
  • Using the wrong mass basis: do not use OD mass with SSD specific gravity in a mix calculation without making the required moisture correction.

Why the Results Matter in Concrete Mix Design

Concrete mixtures are commonly proportioned by absolute volume. Therefore, the relative density of fine aggregate is required to convert its mass into the solid volume that it occupies in one cubic meter or one cubic yard of concrete.

Absorption is also needed when adjusting batch water. Dry sand can absorb part of the mixing water, while wet sand may add free surface water. If this correction is ignored, the actual water-cementitious materials ratio and workability can move away from the design values.